by sparx »
Mon Jun 09, 2008 4:20 pm
Hi Danny,
it used to be permitted to wire detector/call point wiring in standard tw/e.
but for several years now all wiring for fire alarms [as opposed to smoke detectors] must be in fire cable. most popular type is known as FP100,
it must be terminated with correct fire rated glands at panel & should be clipped or otherwise supported by correct fixing method eg not just put in self adhesive mini-trunking,
BS5839 part 1 or 6 apply with certs. similar to electrical ones to be issued ie G1 design, G2 install, G3 commission, G4 acceptance for handover to client.
Eric mentions MICS Pyro type which is still used in places such as shopping arcades but is expensive and slower to install so not used as much, we have installed around 80 systems over the last 3 years, many with radio signalling of activation to monitoring station, nice work if you can get it!!!
regards SPARX