There is great emphasis with the introduction of the 17th edition of the regs on complying with manufacturers instructions.
If this towel rail is existing & has been for a while according to the 16th edition there was no requirement to protect it with an RCD UNLESS the manufacturers instructions required otherwise, so do check them for the requirement.
However what WAS required was equipotential bonding within the bathroom, which is a 4mm earth wire linking all exposed metalwork(such as central heating radiator, metal towel rail and all the pipework supplying the bath & wash-hand basin) with the earth terminals in all load bearing fixed equipment within the bathroom( light fitting, shower,downflow heater etc etc) to ensure that no two accessible metal parts have different potentials(voltages) which would result in a potentially lethal current flow through your body.
If this is not existing it will need to be installed as a minimum requirement and cannot be done by yourself, as it is within a room deemed to be a special location and needs a certificate to be issued on completion, which will then need to be notified to the local authority.
A local Part P registered electrician will be able to do this work for you and advise on timeswitch at the same time.