Thu Oct 11, 2007 8:22 pm
Hi Remelad, no worries, with a Ze 0.42ohms, you won't get into kA region. just line through the 'k'.
Test sheets are set up for in town, close by sub station readings!!
Here in 'the sticks' it's rare to get kA readings, also some meters do 2 readings at once, they read PSCC at highest of either L-N or L-E and Ze @ L-E so maths don't always add up, in fact only TN-C-S systems work out as N&E effectively the same thing.
Glad to see you're still out there, not seen you for a while , Best Wishes SPARX