Hello,

I'm stumped and it is probably quite simple! I went to a job today, Worcester Bosch Greenstar junior 24i combi.

Hot water - check
Call for heating - check ... but wait a minute... no heat from the rads...

after about 20 seconds the central heating cuts out but doesn't go to fault code. The diverter valve is fine doing its job.

I put the big kettle into service mode to fire up central heating on full blast, comes on for 20 seconds and goes off, doesn't re light, no fault code.

The pump is red hot, the flow pipe is red hot, the return pipe is ice cold, is there a blockage?

I know i'm being an amateur here. My thoughts are it is blocked somewhere on the flow pipe. Pipes start at 22mm and are on Microbore to all the rads, not all rads have TRV's and all lock shields open. I emptied out the system, filled her back up, still nothing. I haven't got power flushing equipment so i'm uncertain how to clear it now even if it is a blockage. HELP!!!

Goes to prove that even though I can fit them, doesn't mean I can always fix them!

Cheers for help,

AH.

nitro23456
Foreman
Foreman
Posts: 346
Joined: Sun Aug 12, 2007 7:19 pm

by nitro23456 » Sat Oct 11, 2008 7:33 pm

gotta be a blockage or airlock really.

Steve the gas
Site Agent
Site Agent
Posts: 780
Joined: Sun May 04, 2008 8:07 am

by Steve the gas » Sat Oct 11, 2008 8:37 pm

Take the big screw out of the pump for a minute whilst its running

screech
Ganger
Ganger
Posts: 56
Joined: Tue Sep 02, 2008 10:51 pm

by screech » Sun Oct 12, 2008 12:18 am

i've had pumps pack up on these without a fault code coming up

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Sun Oct 12, 2008 12:48 pm

If all radiator valves are open, boiler flow and return isolatio valves open and you have vented the pump.

I'd be looking towards the pump being the fault, it may be a broken impeller or just a faulty motor - enough to circulate the water around the boiler for the hot water but not for the heating.

htg

AdamsHeating
Ganger
Ganger
Posts: 121
Joined: Fri Aug 08, 2008 11:49 am

by AdamsHeating » Sun Oct 12, 2008 4:55 pm

cheers for the help you lot, I'll check the pump and see if that is playing up.