by ericmark »
Sat Jan 30, 2010 10:02 am
Table 4D2A in BS7671:2008 lists reference methods A, B, C and E. Table 4D5 covers flat twin and earth. There are 4 main reference methods plus C and A and for 10mm cable
Reference Method 100# (above a plasterboard ceiling covered by thermal insulation not exceeding 100 mm in thickness) 45A
Reference Method 101# (above a plasterboard ceiling covered by thermal insulation exceeding 100 mm in thickness) 36A
Reference Method 102# (in a stud wall with thermal insulation with cable touching the inner wall surface) 47A
Reference Method 103# (in a stud wall with thermal insulation with cable not touching the inner wall surface) 32A
I will guess you have been reading some obsolete copy of BS7671? Although likely you can only use a 45A MCB showers are used for such a short time likely you can draw 50A without it tripping.
Cable rated at 90ºC will have higher current ratting but one has to consider where it is routed and can that also take 90ºC. Ali-tube cable to BS 8436 Guardian, only to 6mm² Earthshield, only to 2.5mm² Flexishield, 10sq.mm and 16sq.mm available on request but your not likely to be using enough. Afumex only to 6mm² and so not suitable there are other XLPE (Cross-Linked Polyethylene) or LSZH (Low Smoke Zero Halogen) cables. Because it is hard to terminate 16mm² cable using 10mm² XLPE may be an option but this is something for your electrician to decide.