by johne449 »
Fri Jan 18, 2008 12:19 am
Hi Dave,
I agree with most of what kbrownie says, however, I believe and backed up by reference books such as the IEE electricians guide to the building regulations, that the cable does not need to be protected with metal channel etc although it might be a good idea.
BS7671 522-06-06
offers cable protection by metal channel etc as a method
- but section iv states
Where the cable is connected to a point , accessory , or switchgear on any surface of the wall or partition, the cable may be installed in a zone either horizontally or vertically to the point, accessory or switchgear.
It is however crystal clear that any diagonal runs must be 2" deep or protected.
Regards