by ericmark »
Wed May 25, 2016 11:16 am
Red to Brown connect to L which stands for line.
Black to Blue connect to N which stands for Neutral.
Green, Green/Yellow, or bare together on the E terminal stand for Earth.
However there is still likely a fault even if it starts working again. In the UK we use a ring final system in the main, this allows use to use thin cable 2.5mm sq to supply many sockets from a 30A fuse or 32A MCB, the whole idea is the sockets share the double supply. Testing every 10 years (3 in Scottish rented property where it is now law, but not law in rest of UK) what was called a PIR (periodic inspection report) now called an EICR (electrical installation condition report) or change of occupant, ensures that if the ring is broken then this is found, other wise overloading of the cable can happen and cable damage result.
With the exception of kitchen we don't tend to load a ring final to the limit so even when the ring is broken often nothing untowards happens. One quick fix is to use a 20A MCB instead of the 32A MCB so you have two radials rather than one ring final. If the sockets come from a 20A MCB or fuse you have no worries.
There is a 4mm radial circuit used some times which does use a 32A MCB/fuse but these are rare.
Fault finding can be hard, some times one is lucky, but it can take a long time removing all sockets looking for the fault and testing with a cheap meter. As an electrician we have a special meter called a loop impedance meter, it is not designed to find these faults, but often it can reduce the time taken as we just plug in rather than remove all sockets, and use some experience to guide us to the faulty one.
Sorry it is not just a case of if it works it is OK, but at least you now know it needs further work assuming the MCB/RCBO/Fuse is 30/32 amp.