You state "Not low voltage" do you realise that low voltage AC is 50 ~ 1000 volts and below 50 volts is called extra low voltage, and 63 - 0 - 63 or 55 - 0 - 55 is called reduced low voltage?
So if you have terms correct I am thinking your going to use 12 volt lighting? Daft as it seems Part P still applies to extra low voltage.
So let us look at the main problem. Today we need metal consumer units and RCD protection, so if the main consumer unit is changed in the house then the supplies from out buildings can either have RCBO's in the house, or fit RCD's in each outbuilding. The RCBO option is likely the cheaper, as you can take say a 20A supply to each outbuilding and use a switched FCU for the light switch so the out building does not require a consumer unit.
However having the supply to out building not protected with a RCD in the house but having a RCD in the out building may be better than having to go inside the house to reset. However one would hope you don't need to reset very often.
The RCBO in house does mean the cable to outbuilding is protected so that is the way I would go. The make of consumer unit is limited if you want RCBO's which have double pole switching. You can get RCBO's with double pole switching which are still only one module wide, the neutral current is not monitored by the device but it still switches it with the line, this means a fault in the out building will not affect anything in the house.
Since it is normal to use 2.5mm cable for sockets if using a radial then 25A is limit and if using a ring final then 32A is the limit. If you daisy chain the outbuildings then either all need to be rings or all radials not all consumer units have the option of 25A RCBO or MCB so likely jumps 20A to 32A.
So step one is work out load, you have lets say 4 stages.
13A max you can use fuse connection units (FCU) for supply, not need for any fuse in out building thinner cable and you could even use a RCD FCU and power out buildings before you change house consumer unit.
20A you will need something to reduce max amps for lights, a switched FCU will do, you can have sockets on a radial.
32A now sockets need to be on a ring final.
Over 32A need consumer units in out building.
Remember house supply is 60, 80 or 100 amp, so having a large supply to garage could mean you blow the main fuse, if some one uses the shower in the house.
My garage is integral my shed is fed from a 13A supply, I am unlikely to ever exceed 13A.
Cable size depends on distance as well as current, fridge or freezer needs a supply which does not have a large volt drop, although less than 100W run they use maybe 2000W on start, unless inverter type, volt drop can cause overload to fail. So do say if freezer is to be used.
I would likely daisy chain out buildings as unlikely to use all at the same time. But one has to work out volt drop and routes.