by ericmark »
Thu Feb 09, 2017 1:59 am
Cable sizes have changed over the years, it was diameter and number of strands, now it's the cross sectional area. In real terms getting a micrometer on the cable does not work, what you want is some lugs, so red is 1 or 1.5 mm and blue 2.5 mm and yellow 4 or 6 mm and if slack or tight will show 4 or 6 mm. After that it's stamped on the lug.
Once you know the size the next step is type, some cable is rated 60 degs C normally flex, then 70 degs C standard twin and earth, (PVC) and 90 degs C for the like of ali-tube cable (LSZH). Mineral insulated can go even higher but the problem is even if the cable can run at 250 degs C at that temperature it would likely set other things on fire.
Then we have the route, there are letters to cover most routes, but twin and earth has 100, 101, 102, and 103 this
http://www.batt.co.uk/upload/files/curr ... 876143.pdf link to Batt cables shows how 2.5mm cable can carry between 13.5 and 27 amp. For a ring final we need 20 amp cable so with 2.5mm either method 100 or 102 which limits insulation to no more than 100 mm thick. It also in the regulations shows how it should be clipped as if clipped to even a wooden beam that beam will help dissipate the heat.
Looking at the Batt cables spec it would seem you have 6 mm cable. But since you say white and earth is green/yellow not bare this could be wrong.
In free air or perforated cable tray 2.5mm LSZH cable can go up to 36 amp. This
http://www.batt.co.uk/products/view/684 ... 00V-BS7211 is a link to that cable which is often white.
There are other manufactures but I tend to use Batt cables site myself. I really cringe when I go to places like B&Q and it says 2.5 mm is 21 amp cable, it's not that easy. We also need to compensate for heat and running cables together, but not really with domestic unless run with hot pipes.