by kbrownie »
Tue Jul 04, 2017 8:37 pm
Yes, should have really noted down and marked up cable's original positions.
The problem is we do not know if they where originally terminated as what is the normal process.
I would GUESS, that all the reds are in a loop, they are not directly connected to the new fitting but in a spare/separate connector and terminated together.
Then one would expect the two blacks that are twisted together to be the neutral loop, these would be both terminated at the neutral side of the light fitting. Then you have greens/yellows which should be the CPCs (aka earth). These are terminated together at the earth terminal of the light fitting.
You are then left with a single black core, I would normally expect this to be the switch line, it should be identified though and marked with a red over-sleeve. Then terminated to the live of the fitting.
The above is the normal way that a ceiling rose is wired using two core (red&black) and earth.
It is recommended that you do test the cables to establish what they actually are, also if you are installing metallic or class one fittings, it must be verified that a fault path to earth exists.
.