by ericmark »
Thu Dec 20, 2018 9:58 am
I will guess lock shield valves not set up correctly.
Starting with a radiator that works, nearest to boiler, turn off lock shield valve (tap opposite end to TRV) allow pipes to go cold then with boiler running and TRV set to max, open 1/4 turn at a time with couple on minutes between each turn, until you feel hot water in either of the pipes, then stop, normally around 2.5 turns.
Then repeat for each radiator slowly moving away from boiler, water takes easiest route, it's not the radiators which don't work that is problem, it's the radiators that are work have too much flow.