by ericmark »
Mon Jan 07, 2019 2:58 am
In Europe they don't have a fuse in the plug, and don't use the ring final system, to use an European appliance designed for a 16 amp supply you need a dedicated supply from the consumer unit.
Some house today do use the radial system, and if that is the case you may be able to get a 15 or 16 amp socket fitted, but since in the main we use the ring final system, in the main we are not permitted to fit a 15/16 amp socket as the supply protective device (fuse, MCB, RCBO) is to large to allow connection.
Unfortunately you can't get a fuse connection unit with a 16A fuse, so you will likely need a dedicated supply, this is unfortunately common when you use European products.