Unexpected voltage
Ask questions and find answers to many subjects relating to electrics and electrical work

4 posts   •   Page 1 of 1
sunny
Apprentice
Apprentice
Posts: 6
Joined: Thu Jun 14, 2007 1:01 pm

Unexpected voltage

by sunny » Sun Sep 02, 2007 11:52 am

Hi, I am recently part P qualified, still with a lot to learn. Not a real spark just a fitter who decided to become legal!!

I was testing a celling rose for a fault (turned out to be the switch), across the bulb with the switch on was 240v as you would expect. When the switch was turned off though, there was still around 30v present. This doesn't seem right, any ideas?
Sunny.

andy.blackpool
Apprentice
Apprentice
Posts: 20
Joined: Sat Aug 25, 2007 12:04 am

by andy.blackpool » Sun Sep 02, 2007 7:22 pm

no, it doesnt. u need to check the circuit and your equipment

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Sun Sep 02, 2007 11:06 pm

Hi. If you are using a cheapish digital multimeter then try gripping the two probes & see what you read!!
These meters are always looking for some reading, and will pick up induced voltages from neutrals etc, if you tried with a moving coil analogue meter bet it wouldn't move!
This is why regs. require use of approved mains testers ie multi neon type for live checks, it's a steep learning curve, don't lose heart,regards
SPARX

sunny
Apprentice
Apprentice
Posts: 6
Joined: Thu Jun 14, 2007 1:01 pm

by sunny » Mon Sep 03, 2007 10:57 am

Thanks for that SPARX, I'm trying to do all the learning I can. But I was using my expensive part P approved and calibrated voltmeter, possession of which as you know is a requirement of part P. So I guess there really is 30v across it?

4 posts   •   Page 1 of 1
It is currently Sat Nov 23, 2024 2:15 am