central heating switches itself on
Help and information on all topics relating to your central heating, air conditioning and ventilation issues.

6 posts   •   Page 1 of 1
griersona1
Labourer
Labourer
Posts: 3
Joined: Wed Mar 28, 2007 12:55 pm

central heating switches itself on

by griersona1 » Wed Mar 28, 2007 1:12 pm

Hi

The gas central heating system does not always switch off. The electronic timer switches the heating off but the central heating pump still runs and the gas boiler cycles on and off. the wall thermostat has no effect.

At the moment this is happening at night (uncomfortable sleep) but can happen in the day. the electronic timer has recently been replaced but this fault was there before.

peter the plumber
Ganger
Ganger
Posts: 197
Joined: Wed Mar 28, 2007 10:19 am

by peter the plumber » Wed Mar 28, 2007 6:03 pm

I think what’s happening here is your boiler is working to keep your cylinder warm and not your radiators.

If you have thermostatic radiator valves, you need to have a by pass radiator on all the time, so the boiler does not over heat if there all reach the right temp.

If you have a frost thermostat, that could be the reason too.

If it’s a wireless thermostat, it could be confused by other signals.

Or it could be a faulty board in the boiler.

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Wed Mar 28, 2007 8:57 pm

you don,t say what system you have ie combi, or more likely standard boiler with three port valve for heating and hot water. if so valve may have stuck . another possibility is if boiler is in outhouse or garage is there a frost stat fitted?
give us a clue...........
SPARX

griersona1
Labourer
Labourer
Posts: 3
Joined: Wed Mar 28, 2007 12:55 pm

by griersona1 » Thu Mar 29, 2007 9:24 am

Hi

The boiler is a standard gas boiler, not condensing or combi, about 7 years old on a three port valve for heating and water. There are thermostatic valves on all radiators and more than one is open fully. The boiler is located in the kitchen. My initial suspicion was a stuck valve but it seems to follow a pattern of night time and certain times of the day.

Cheers

Andrew

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Thu Mar 29, 2007 9:44 pm

try: when house cool turn cylinder stat down to make sure it's not calling boiler, then with ch on prog. set to on room stat should turn boiler on and off, note pump may run on for a while after boiler shuts off this is normal so check at boiler not pump.
if no control suggests room stat u/s

griersona1
Labourer
Labourer
Posts: 3
Joined: Wed Mar 28, 2007 12:55 pm

by griersona1 » Mon Apr 02, 2007 12:52 pm

HI

This has turned out to be a faulty circuit board in the gas boiler which as now been replaced and it appears to be working ok, (at least till I submit this)

Cheers