by ericmark »
Mon May 18, 2020 8:04 am
I have not used sonoff as yet, but as far as I can tell the unit is connected to the ceiling rose not the light switch and the S1 and S1 wires become the switch wires so you are it seems switching extra low voltage at the lights.
My son has suggested I use sonoff or another one which does the same, but for me only really an options for upstairs lights as no access to behind ceiling rose on lower floor.
Other makes also have problems with two way lighting, the standard way to use two way lighting is [attachment=0]two-way-real.jpg[/attachment] shown, there are three wires between the two switches line in bottom and line out top, the middle wire between the two com is the problem, in the diagram shown it carries 230 volt.
However with electronic switches this includes dimming switches and smart switches that middle wire is a data wire, and connects between the S terminals of a slave and master, and it is because you have slave and master switches that we have a problem, all the two gang switches are either slave or master, they never seem to make a switch where one switch in the plate is slave and one switch is master.
I think however you could use a slave/master combination but the cost is much more than using the sonoff for example Energenie.
Gateway £70 CODE: MIHO001
Slave one gang £15 CODE: MIHO043-S
Two gang master plus one gang slave £60 CODE: MIHO090
So £145 for all three, compared with around £15 for two sonoff units fitted in the ceiling, and all the non neutral switches and Energenie does not need a neutral, have a problem with some LED lamps, the standard BA22d bulb seems to work OK, but some of the smaller bulbs specially the G9 have problems one when switched off they can flash, although a load capacitor can cure that, but also when switched on some flicker, only cure I have found is swap one bulb for quartz.
Using switches which need a neutral is far better, if you have a neutral at the switch, many of the cheap wifi connected switches have a single supply to all switches on the plate, that can also cause problems where the lights are supplied from different fuse/MCB/RCBO in my house when I first fitted all RCBO protection I found one switch where the wrong line was used (technically called a borrowed neutral) lucky I was able to correct at the light switch, but I know I have a 4 gang light switch which has two line supplies one for upstairs and one for down stairs so could not use a switch which combines all lines feeds.
Note we call the phase conductor in single phase line, as the neutral is also considered as live just in case you wonder what I means when I say line.
-