by DIYmonks »
Fri Oct 23, 2020 4:41 pm
I have had a new Vaillant boiler fitted a year ago. I had no problems with it until I fitted a new radiator. I switched off the boiler, drained the system, fitted the new rad, filled up the system adding the correct inhibitor and re pressurised it up to 1.5 bar and then closed off the filling loop valves. All the the rads have been bled and it runs well with no leaks, but I am losing pressure after a few days. I have had to open up the filling loop several times. The PRV is dry and I have checked and rechecked for leaks too. Could it be the expansion vessel leaking? As I said the boiler is 1 year old and I am thinking of getting it checked under warranty but I need to make sure I haven't forgetten to do something before I go down that path. Thanks in advance.