Hot water pressure problem with unvented hot water system
Drainage and wastage systems and plumbing help, advice and answers

3 posts   •   Page 1 of 1
rbtisa
Labourer
Labourer
Posts: 2
Joined: Fri Dec 04, 2020 4:52 pm

Hot water pressure problem with unvented hot water system

by rbtisa » Tue Dec 08, 2020 6:01 pm

I have a unvented hot water system & when the hot water is turned on the pressure is as good as it was before a new expansion vessel was fitted, however after 5 > 10 seconds it drops to a level which is Ok but not brilliant. The expansion vessel pressure is set at 2.1 bar (as was the old one) which is the pressure recommendation on the hot water tank, the reducing valve is also set at 2.1bar. Could the reducing valve be faulty ? or could a air lock be causing the problem ?

stoneyboy
Project Manager
Project Manager
Posts: 6535
Joined: Wed Dec 10, 2008 6:44 pm

Re: Hot water pressure problem with unvented hot water system

by stoneyboy » Wed Dec 09, 2020 7:58 pm

Hi rbtisa
The pressure control valve would seem to be the issue but do check all valves which may have been shut for the EV replacement are fully open.
Regards S

rbtisa
Labourer
Labourer
Posts: 2
Joined: Fri Dec 04, 2020 4:52 pm

Re: Hot water pressure problem with unvented hot water system

by rbtisa » Wed Dec 09, 2020 8:20 pm

Thanks for the reply S
All valves are fully open so I might replace the reducing valve with one which is fitted with a gauge, at least that way I'll know if the tank is at the correct pressure.