Wiring New ProTouch Smart Room Thermostat to Replace old Danfoss
Help and information on all topics relating to your central heating, air conditioning and ventilation issues.

7 posts   •   Page 1 of 1
kpgristy
Labourer
Labourer
Posts: 4
Joined: Sat Feb 27, 2021 4:45 pm

Wiring New ProTouch Smart Room Thermostat to Replace old Danfoss

by kpgristy » Sat Feb 27, 2021 5:03 pm

Help. Have a Danfoss room thermostat for underfloor heating that no longer seems to be programmable. Want to replace with a smart thermostat. Got a ProTouch Smart.
The old Danfoss had 3 wires connecting. Grey into (N)eutral, Black into NC/Normally Closed and Brown into (L)ive.
The new Protouch has Neutral, Live, NO/Normally Open and COM contact points.
I assumed to wire it, it would be Grey/Neutral, Brown/Live... and the Black into either the COMM or the NO. Whilst the thermometer powers up and connects to WIFI ok, it doesn't trigger the boiler to heat the room. I will call an electrician in, but posting here in case there is an obvious solution. Thanks in advance.

stoneyboy
Project Manager
Project Manager
Posts: 6536
Joined: Wed Dec 10, 2008 6:44 pm

Re: Wiring New ProTouch Smart Room Thermostat to Replace old Danfoss

by stoneyboy » Sun Feb 28, 2021 10:25 pm

Hi kpgristy
There should be two connections either side of the com connection. One should be nc and the other no. You may have to provide a live feed to the com connection but refer to the installation instructions.
Regards S

kpgristy
Labourer
Labourer
Posts: 4
Joined: Sat Feb 27, 2021 4:45 pm

Re: Wiring New ProTouch Smart Room Thermostat to Replace old Danfoss

by kpgristy » Mon Mar 01, 2021 8:29 am

Thanks Stoneyboy. Alas there are just the 4 points and no NC. See image. Live and neutral connect fine... thermostat lights up, connects to WI-FI and is programmable. It’s just that when it calls for heat from the boiler, it gets none. Boiler etc are ok as the previous thermostat call for heat fine. Is the issue purely that I have no NC contact... which would mean the thermostat is essentially incompatible?
Attachments
3324F591-D751-4A3C-88B9-48A53ECE30DB.jpeg

stoneyboy
Project Manager
Project Manager
Posts: 6536
Joined: Wed Dec 10, 2008 6:44 pm

Re: Wiring New ProTouch Smart Room Thermostat to Replace old Danfoss

by stoneyboy » Mon Mar 01, 2021 10:49 pm

Hi kpgristy
Suggest you wire the stat as shown in the ‘switching mains voltage’ diagram and fit the black wire into the NO connection.
Regards S

kpgristy
Labourer
Labourer
Posts: 4
Joined: Sat Feb 27, 2021 4:45 pm

Re: Wiring New ProTouch Smart Room Thermostat to Replace old Danfoss

by kpgristy » Thu Mar 04, 2021 8:50 pm

Thanks again for responding. I did try that first time around, which ultimately led me to raise this post. I may try again this weekend just in case there was a loose wire, but I’m not holding out much hope.

ericmark
Project Manager
Project Manager
Posts: 2869
Joined: Fri Oct 02, 2009 9:49 pm
Location: Llanfair Caereinion, Mid Wales.

Re: Wiring New ProTouch Smart Room Thermostat to Replace old Danfoss

by ericmark » Sat Mar 13, 2021 1:21 pm

As said new needs link, where old one link internal. So Brown into (L)ine and (Com)mon.

kpgristy
Labourer
Labourer
Posts: 4
Joined: Sat Feb 27, 2021 4:45 pm

Re: Wiring New ProTouch Smart Room Thermostat to Replace old Danfoss

by kpgristy » Sat Mar 27, 2021 11:41 am

Thanks both.... worked a treat. Appreciate your guidance.