MCB keeps tripping in new 10 way Schneider unit
Ask questions and find answers to many subjects relating to electrics and electrical work

4 posts   •   Page 1 of 1
Spence1412
Labourer
Labourer
Posts: 1
Joined: Mon Sep 13, 2021 8:27 pm

MCB keeps tripping in new 10 way Schneider unit

by Spence1412 » Sun Sep 26, 2021 2:23 pm

Just installed a new 10 way Schneider unit.
All ok apart from downstairs ring.
The circuit tests ok.
A mains powered radio and one table lamp work but any more than that and mcb trips.
I have unplugged all appliances and plugged them back in one by one but they all cause tripping.
If there was a short then the radio and lamp wouldn't work would they.
Very confused.
Kevin

Mr White
Project Manager
Project Manager
Posts: 1333
Joined: Tue Jun 20, 2017 10:54 pm

Re: MCB keeps tripping in new 10 way Schneider unit

by Mr White » Sun Sep 26, 2021 9:19 pm

You said
Spence1412 wrote: The circuit tests ok.


What is "OK" and who tested it? and what was it tested with?

Picture of what trips would help.

chriscba
Ganger
Ganger
Posts: 118
Joined: Thu Aug 27, 2009 11:00 pm

Re: MCB keeps tripping in new 10 way Schneider unit

by chriscba » Sun Oct 03, 2021 9:36 pm

Swap the rings over to see if the fault moves to a different circuit.
Then if it has, you have an over sensitive MCB.
So you can change it

ericmark
Project Manager
Project Manager
Posts: 2870
Joined: Fri Oct 02, 2009 9:49 pm
Location: Llanfair Caereinion, Mid Wales.

Re: MCB keeps tripping in new 10 way Schneider unit

by ericmark » Thu Oct 07, 2021 5:12 pm

I have a feeling it is not a MCB tripping but a RCBO or RCD?

I would guess wrong neutral, but as @Mr White says, who tested the circuits to show OK and how?

There should be an installation certificate showing test results, and either a compliance or completion certificate.