A RCBO is three trips combined, the MCB is two trips combined.
So there is a thermal trip, amps shown by a number.
A magnetic trip between 3 and 20 times the valve of the thermal trip, shown by a letter so for example a B6 with trip at under 5 x 6 = 30 amp with the magnetic trip, and around 6 amp given enough time with the thermal trip.
Now the RCBO also has an imbalance trip, it measures amps out and amps in and if these are not within a set amount it assumes some must be leaking to earth.
Most are rated 30 mA which means they must not trip at 15 mA, but must trip at 30 mA and must trip within 40 mS at 150 mA. In the main they trip around 25 mA.
The problem is although the line (live includes both line and neutral) goes through a switch, often the neutral does not, and neutral is around the same voltage to earth, the voltage between neutral and earth depends on the load, so the more load the more likely to trip.
So it is normal to use double pole switches for outside lights, as they are likely to get water in them, although this house they are single pole switches.
Idea is with double pole you can isolate the lights.
Note to isolate both line and neutral must be switched.
This house was wired before the advent of RCD protection, but after 2008 one would hope electricians would use a double pole switch. 2008 was when we started to use RCD protection for all circuits.