Consumer units can have cartridge fuses, but very unusual, can't remember when the type tested distribution unit came out, I think in the 90's before the type testing they were simply fuse boxes.
The problem is although BS7671 is not retrospective, once you do any alterations then it needs to comply with current regulations, and the electrician has to sign to say "I being the person responsible for the Design, Construction, Inspection & Testing of the electrical installation (as indicated by my signature below), particulars of which are described above, having exercised reasonable skill and care when carrying out the Design, Construction, Inspection & Testing, hereby CERTIFY that the said work for which I have been responsible is to the best of my knowledge and belief in accordance with BS 7671:2018, amended to .............(date) except for the departures, if any, detailed as follows."
See page 4 here
https://electrical.theiet.org/media/220 ... ficate.pdfThe electrician has his hands tied, he must issue the certificate you should already have one for the temp repairs, although I would suspect he is considering it as work in progress.
So the ring final must to comply with regulations use cable which can carry 20 amp, in the main that means 2.5 mm² but before we went metric it was 7/0.029 cable which was more like 3 mm² but even 2.5 mm² has a range of current carrying capacity, one down to insulation, mineral, thermal setting plastic, or thermal plastic plastic, and also where it runs, if in any insulation etc. This chart
http://www.batt.co.uk/upload/files/tabl ... 390425.pdf shows same cable can be rated 17 to 27 amp.
We hope everything installed correctly to start with, and nothing has changed, the latter is unlikely, I know as managed to blow a fuse with a line - earth error as a lad my parents house did have a good earth, but some 40 years latter that earth was missing, how and why is guess work, seems likely it used the water main, and the main was replaced with plastic.
So we are told every 10 years, 5 years with English rented, or change of occupant, we should do an EICR (electrical installation condition report) to high light problems, OK hands up not done it on my own house, I suspect few do.
However my house has all RCBO's which is a MCB and RCD combined. The RCD was first used for TT installations (uses an earth rod) but since 2001 the regulations have required it to cover more and more, and have reduced it from 100 mA typical for TT to 30 mA.
This has caused no end of problems, specially with old homes, and we are still moving on with better and better protection, so the S type 100 mA RCD rarely tripped, but the 30 mA type AC has caused so much food to be dumped due to freezer failure one has to really ask has it been worth it.
Major problem was in early years we would group circuits together, so typical home had either just half RCD protected or only 2 RCD for whole of home.
We have moved on, we will use double pole switches for outside lights, and we have learnt the problem of all eggs in one basket, and although some still do only use 2 RCD's most use at least some RCBO's plus with the new breed of electronic equipment where we have semi-conductors on the 230 volt part, the use of SPD (surge protection device) has increased.
No longer do we run cables through the cavity wall, however cavity wall insulation installers seem to fill the wall even if the cables do go through the cavity.
EV chargers and solar panels have added to the problem, and even some central heating boilers now stipulate type A RCD's.
So if you are still using tungsten bulbs, and living in the dark ages, then maybe the distribution unit you have is good enough, but that is unlikely, so your looking at at least £1000 bill to correct the fault and upgrade the consumer unit.
From moving in to this house to getting SPD and all RCBO's took me around 6 months, landlords with rental property were given 28 days to upgrade, but we have to be sensible, better wait 6 months or a year and get it done properly than rushing into it and loosing a freezer full of food.
So now is the time to plan when, you have had the wake up call, now time to plan what you will do in the future.