Yes ring final designed end of WW2, been some changes, smaller cable when we went metric, and insulated plug pins which reduce the heat transferred into the socket, and gone from fuse to MCB/RCBO and 30 amp to 32 amp, and dropped from 1.44 ohm to lower figure 5% less, and volt drop changed from 4% to 5%.
The main change however was the 1/3 rule drilling beams for cables, so we ended up with more cable, but the cost of RCBO verse MCB means having fewer circuits means less cost, so although there was a move to radials, this has reversed.
Traditionally we were allowed 88 meters of cable on a ring final, the change in volt drop resulted in this being extended to 106 meters, the formula does not seem to have been published, but was 20 amp centre and 12 amp even spread, so worked on 26 amp load when calculating volt drop.
The problem with the radial is it still has 20 amp at final socket, so you need three radials to do same area as one ring final.
I was worried about volt drop, and some one coming back to me and saying the volt drop has been exceeded, so I wrote a program to work out volt drop using the loop impedance, however once written it was clear the accuracy of the loop impedance meter was a major problem, and one could have 150 meter of cable before anyone could prove you had made an error.
And in the real world I have only once found a problem with volt drop, a shrink wrap machine failed to work due to volt drop.
In the main the switch mode power supply has resulted in volt drop not being a problem, old freezers and fluorescent lamps with magnetic ballasts have traditionally been a problem, but the inverter drive used on modern freezers and the electronic ballast used with fluorescent lights have removed this problem.
However the 5 year EICR required with rental property has raised a lot of issues, as electricians the last thing we want is for some one to say "I have had an EICR done, and your work has failed".
However the forms suggested by the IET do not show volt drop, or any reading which can be used to show volt drop, seems wrong, and likely they will realise and alter the standard forms.
However the meters required to show the loop impedance is within limits are darn expensive, so unlikely any DIY person will have them, even a plug in tester with loop and RCD test costs over £50, and only tests to 1.7 ohm and 200 mS when it is required to be under 1.4 ohm and 40 mS, although personally I would not be worried.