by ericmark »
Tue May 07, 2024 10:39 am
The regulations refer to a tool or key, and if it needs a tool or key to change the bulb, then the person using the tool or key should isolate first, this means turn off all live feeds, which include both line and neutral, so the light switch only switches line so does not isolate.
Yes I know that seems daft, but it is what the regulations say.
As to the regulations, the requirement for the earth arrived in 1966 it said "D.6 At every lighting point an earthing terminal shall be provided and connected to the earth-continuity conductor of the final sub-circuit." before it said "403 The application of Regulation 401 (iv) which exempts from the requirement of earthing metal which is so isolated that it is not liable to come into contact with live parts or with earthed metal, shall be restricted to the apparatus detailed in the following \clauses (i)-(ix):
(i) Short isoated lenghts of conduit used for mechanical protection of tough-rubber- or p.v.c. -sheathed wiring.
(ii)Short unexposed isolated lengths of metal conduit used for the mechanical protection of cleated wiring where it passes through floors, walls, partitions or ceilings.
(iii)Short isolated lengths of catenary wire used with tough-rubber-sheathed or p.v.c.-sheather wiring systems, if screened by non-conducting material.
(vi) Lamp-caps.
(vii) Small parts such as screws or nameplates isolated by insulating material.
(viii) Metal chains for the suspension of lighting fittings, not in contact with flexible cord of the twisted type.
(ix) Lighting fittings using filament lamps installed in a room having a non-conducting floor, mounted at such a height that they cannot readily be touched and are out of reach of earthed metal." and today "A circuit protective conductor shall be run to and terminated at each point in wiring and at each accessory except a lampholder having no exposed-conductive-parts and suspended from such a point.".
So wall lamps have needed an earth before 1966 and today if the lamp is not suspended then needs an earth at the accessory, so not to fit an earth would not comply. But it also says "134.1.1 Good workmanship by competent persons or persons under their supervision and proper materials shall be used in the erection of the electrical installation. Electrical equipment shall be installed in accordance with the instructions provided by the manufacturer of the equipment." so one assumes the type testing has identified some risk when fitting an earth.
However I think it is more likely that it has been translated from Chinese and a mistake has been made in the translation. Many thermostats have a parking terminal for the earth, and the same with down lights, so I would be asking the question at the "well known retail supplier" I am always weary of ES bulbs, the screw should be neutral, but so many use same colour for line and neutral often hard to comply without getting the meter out.