no circulation in additional radiators

by bernie » Fri Oct 12, 2007 1:15 pm

I have a single pipe heating system, and installed additional radiator which will not heat up. I have taken the supply from in the loft and come down to the ground floor, through radiator with bypass and tied back into the system on the ground floor. The radiator filled and was able to bleed all of the air out. It appears that there is no circulation, so maybe is being fed from both tie in points?. What can I do to make it work?

The Heating Doctor
Foreman
Foreman
Posts: 214
Joined: Mon Aug 27, 2007 10:49 am

by The Heating Doctor » Sat Oct 13, 2007 2:10 am

Are the radiator valves you fitted specifically designed for one pipe systems? How have you piped to the radiators? What size of pipe have you used. Has the pump the capacity to take an extra radiator?

bernie
Labourer
Labourer
Posts: 2
Joined: Fri Oct 12, 2007 1:02 pm

by bernie » Mon Oct 15, 2007 8:21 am

The original piping is in 3/4", I have tied in with 15mm. The pump I believe is large enough as the old system worked set on 1 and I have change the setting to 2. The valves are just normal standard valves prchased with the radiator. Hope this helps.

The Heating Doctor
Foreman
Foreman
Posts: 214
Joined: Mon Aug 27, 2007 10:49 am

by The Heating Doctor » Mon Oct 15, 2007 9:56 pm

I beleive that is where you problem lies, one pipe systems require very specific equipment to operate. i.e. low loss radiator valves.
The radiator valves should be large oriface valves or 3/4" as this will provide the low loss required. Search internet for one pipe radiator valves.
Hope this helps you.