by htg engineer »
Fri Nov 02, 2007 3:10 pm
It could be the spark electrodes need cleaning or re-positioning, this is where the spark is to light the pilot or main burner.
Haven't came across your boiler before,
does it have a pilot light ?
or does the spark electrode light the main burner ?
is it a fanned flue boiler ?
if it has a pilot, it may be the injector is blocked or the pilot needs adjusting, on some older boilers with electronic pilots the fan pulls the gas away before it can ignite this also happens with the flame the fan pulls the flame away from the thermocouple/flame sensing electrode.
Is it dues a annual service, if so get it done and ask them to repair this fault while they're there.