by sparks »
Mon Nov 05, 2007 8:59 pm
multi meters are not usually used for testing earths a low resistant ohm or continuity meter is used for this ,some multi meters are not accurate enough for this purpose, so how do you check ,regulations state that bonding to any service should be made within 600mm of the incoming service water gas etc. bonding should be made to basins and baths pipe work and radiators in bathrooms.the main bonding to water should be a minimum of 10mm with any supplimentry bonding 6mm . to test the earths ,ensure the supply has been isolated and disconnect the earth ,connect an earth to the earth bar at the mains board then test between that cable and the point of connection to the incomming service ,this method is know as the long lead method ,once test carried out dont forget to reconnect the earth