by picky_paul » Sat Nov 10, 2007 11:58 pm

I have fitted a new low volts mulitple halogen light. It is driving me nuts. Every so often the MCB on that specific lighting circuit trips.

I tend to think it is the MCB which is an old 5A MEM Type 1 trip. Problem is I can't find a replacement MCB to fit in the same consumer unit.

Is it likely to be the trip? Are there compatible replacements out there?

BLAKEY1963
Site Agent
Site Agent
Posts: 684
Joined: Wed Jun 13, 2007 11:57 pm

by BLAKEY1963 » Sun Nov 11, 2007 9:19 am

pickypaul
not being awkward here but , with power isolated have all connections been checked for correct polarity , and r they tightly
connected . if insulation resistance tests on cable only , with no loads
connected , have come out okay , and r1 + r2 to check you r adequately
earthed ( also obtaining an earth loop reading to confirm integrity of earthing )
then u could have a faulty transformer or the MCB could be faulty.

BLAKEY1963

sparx
Project Manager
Project Manager
Posts: 2166
Joined: Wed Mar 21, 2007 8:33 pm
Location: The fifth continent.

by sparx » Sun Nov 11, 2007 8:04 pm

Hi p-Paul, I think you may be right abt. type 1 mcb as don't allow much 'inrush' current b4 tripping & halogen types are high inrush load,also 5A only allows abt. 1000W total load so may be combination of both, unfortunately as you say no suitable replacements for old type,