by cal »
Fri Nov 16, 2007 5:19 pm
The boiler is a baxi system boiler 60/100, the heating is an unvented sealed system, with open vented hot water cylinder and tank.
External controls are;
Siemens RWB9 programmer (working), Boss therm room stat(eliminated),
Boss therm cylinder stat (working)
Newly replaced Honeywell 3 port valve, old was Boss therm with same wiring.
The problems with this system have apparantly been from day one, boiler is around 7/8 years old.
To start with the old 3 port valve had been placed in manually open position, probably to disguise the fact when in auto it didn't work, Honeywell replacement now fitted, which has cured that part of the problem.
Then 2 non working radiators have been cleansed of sludge and the system cleansed and is now hotter than ever.
Really everything works fine until the programmer is put into CH on mode,
after that nothing will turn it off, except the fuse spur.
So my thinking is to try and find what is holding the boiler on, but i'm running out of ideas.
To clarify, if boiler is then switched back on, with programmer off, boiler behaves correctly and nothing happens, with HW on, boiler fires, diverts correctly cylinder gets warm, cylinder stat turns boiler off or programmer turns boiler off, only when CH is on, and then switched back off, the boiler keeps going!
Any ideas, questions, points i've missed, please post.