If balancing the rad.with just IRV's ( bathroom or hall location common), try continuing balancing the rest of your rads. to put pressure onto the cool rads. If that doesn't work, then it is possible that your system needs flushing/rinsing to remove flushing chemicals/then refilling with a fresh charge of plain water dosed with corrosion-inhibitor. Unfortunately, it is not unusual for new systems to be installed without the above commissioning procedure being carried out, as it is so time-consuming.
Cleanser needs to be flushed out until all rads. drain out clear, as the chemical automatically becomes neutral after a few weeks and then all the flux & oil etc. taken into solution by it starts to precipitate out. Anti-corrosion additive is essential, especially now that aluminium is being used in boilers, and needs to be kept up to strength ;--- have it checked at the annual service.
I can personally vouch for this cowboy attitude existing in the trade, as my brand new system was left 10 days with plain water in it, and after complaining, they put both cleanser and inhibitor in together. They really do think the public are fools. Only a telephone call to the manufacturer of the chemicals clarified the required procedure. They are being recalled to flush the system fully, and recharge with inhibitor-doped water.