by sparx »
Tue Dec 11, 2007 5:12 pm
Hi.
each shower would take 37Amps, potentially if all on together could draw 148A except that the largest single phase domestic supply is fused in cut-out at 100A!
The fact that your main sw. is rated at 100A is irrelevant to the problem, as if sufficient spare 'ways' in board are available then you can't overload board as company fuse will blow first.
Showers should be RCD protected so maybe a second C.U. may be an answer with an RCD as main sw. the 'tails' will still go to same supply via a 'Henley Block' connector so still only got 100A to play with, however you can allow for some diversity ie not all will be in use at same time, which is what supply authority allow for eg when calculating for a new housing estate they work on an average load per house of around 20A i'm told, otherwise the cable sizes, transformers ect. would be huge.
see what the 'part p' leckies have to say and maybe repost their solutions before commiting.
must you use electric showers? no pumpable hot water?
regards SPARX