I am to supply a house with a new power feed but having difficulty with rating the armoured cable size.I also have a few more question if anyone can help.
1.The Scenario:A main meter head is being moved and fitted to the external garage (disconnected from the house).I am to take a supply from there back around the house and stab in through the wall and provide power to the basement at the DB. I was under the impression that I had to run armoured of 25mm cores but I have just checked on a web page (TLC) and it is saying that 16mm (2 core) armoured cable carried 110A. The diversity of the house has been worked out to under 100A and the main fuse will be 100A.I am just curious if this would be sufficient?Its plain obvious it WILL but I was looking for confirmation from the experts.
2.Also with the earthing- would it be sufficient if i took the main earth off the armoured sheath from the meter head, through my armoured and into my DB?
Or should i opt for a 3 core SWA instead and use the 3rd as my earth?
3.Once the meter is moved to the external garage wall,it is to be housed in an enclosure. I was wondering if I put an exact housing next to it and used that as my connections feeding the garage and the house?So I would use that as a sort of junction box.Is this allowed?and do i have that option?if not what else can be done?
Many thanks for your time and patience,
Eternally Grateful.
Sparkydelux