Hi blunun,
It seems to me that you have low design current to your shower, this current would only allow you to run a maximum 6.9kw.
There are a few calculation that need to be done as regards of length of cable, ambient tempreture, whether the cable runs through insulation, if it is grouped with other cables and by what means it is clipped/fixed. For you to arrive at the correct fuse rating
If you wanted to install a 8.5 or 9.5kw rated shower you would need at least a 45amp fuse that's with all calculations being in your favour.
10mm cable okay, (I believe you can put up to 65amps through 10mm cable as long as all calculation allow)
But if you are having shower fitted it comes under part p of building regs and has to be done by an electrician quaified to that standard.
Hope that the info was of use and remember always to be safe around electrics
KB