by htg engineer »
Mon Jan 21, 2008 6:12 pm
When does the pressure rise ?
If it rises when heating is off, possible water to water heat-ex has corroded. This will allow the heating and hot water to mix.
Check the filling loop is closed if an external one is fitted, not sure if this model has an internal filling loop, Do you have to use a white plastic key to re-pressurise ?
If the pressure only rises when the heating is on, then it's probably the expansion vessel needs re-pressurising or replacing.
If the pressure is set to 1.0bar when cold, then it will rise when the heating is on but should remain under 2.0bar.
I know you said it's at 3.0 bar now, what if you left the system running, does it continue to rise ? does is discharge via the pressure relief valve ?