presuming you have notified LABC of your part-p work,
Answer depends on expected load, if we assume 32Amps including lights ect. then for worst case distance, using PVC /SWA table 4D4B gives a volt drop of 4.4 mV /Mtr/Amp or:
4.4 X 70 X 32 =9856mV/1000= 9.8Volts dropped which exceeds allowance of 4% of 240v or 9.2Volts, not forgetting you are only allowed this much to the furthest point of the longest final circuit in garage.
Next consideration would be earth loop impedance to ensure tripping of the supply device, MCB/Fuse, over such a distance it may be difficult to achieve even with 16mm2 only way then is to not connect armouring at summer-house end and use RCD incoming switch with an earth rod,T.T. system.
So either : move summer house closer!, accept lower loading, or go up to
16mm cable or more!. BTW I hope you meant 6A lighting circuit!
SWA can be run directly buried as long as deep enough not to be hit by spade/fork etc. and must be half back-filled then yellow marker tape put over it then final back-filled so someone later finds tape before cable,