by sunny »
Sat Feb 09, 2008 12:14 pm
Sorry chaps, should have given more info from the start.
Yes it is TT and it has always been my intention to have all circuits in the new board on appropriate RCDs
I'm a bit unsure why Rocky says a split load board is unsuitable, I thought that was the norm for a TT system.
I only thought of using the old ELCB as an isolating switch (and nothing else) to save getting the supply disconnected when I change the board. Of course if I change the ELCB for a switch then I am back into that hassle.
I assumed, possibly wrongly, that if the ELCB was of a sufficient rating to switch the whole installation when it was first installed then it would still be good enough now. After all I am not adding any extra circuits or load. Rocky makes the point that it may not comply with current regs, if it doesn't then must it be replaced? This is another generally confusing area. After all you can note things on a periodic as conforming to an earlier edition but that doesn't necessarily mean those things need changing. You don't have to bring everything in a property up to the current regs just because you've changed a light bulb! So when do you need to upgrade and when don't you?
Interesting stuff, thanks for your responses, I look forward to your thoughts.