by ericmark »
Fri Feb 15, 2008 12:39 am
Running cables through the cavity's in partition walls is common but the rules are complex. You need to be 50mm from outside of wall both sides or follow other rules as to how close to corners etc. The main problem is later when the route is forgotten one could drill the wall and hit the cable. Alternative protection methods are given like steel conduit and RCD protection. Work in bathrooms is covered by Part P and anyone signing the installation cert will have to had done the job or supervised it so I would ask who ever is signing the paperwork as competent person as to what routes they would want to be followed.