earth bonding wire size
Ask questions and find answers to many subjects relating to electrics and electrical work

3 posts   •   Page 1 of 1
newartist
Labourer
Labourer
Posts: 2
Joined: Wed Apr 25, 2007 8:24 am

earth bonding wire size

by newartist » Wed Apr 25, 2007 4:21 pm

If installing new earth bonding to pipes in a bathroom what is the correct size of earth wire.
I have heard that it has now been increased to 10mm for new work.

Mill Spark
Apprentice
Apprentice
Posts: 10
Joined: Fri Apr 13, 2007 12:10 am

by Mill Spark » Wed Apr 25, 2007 7:39 pm

Bonding in bathrooms is internal to the bathroom only – so there is no need to run any earth cables to the CU.

Bond together all pipework, and take this to the cpc of each circuit that enters the bathroom.

So for example if you had a shower, heater, lights and fan. You would run a 4mm cable from either the light switch, fan, light fitting, shaver point to either the shower or shower switch, and then to the heater. This would also be connected to the pipework.

You dont need to bond to metal pipework which is fed via plastic pipework, as long as the transition is in the bathroom. You don’t need to bond a metal bath if it is fed via plastic pipe and plastic waste.

It can be quite logistical deciding how and what to bond, as each bathroom is different.

A guide can be found here

[url]http://www.iee.org/Publish/WireRegs/EarthingPlasticPipes.pdf[/url]

Hope this helps
Andy

newartist
Labourer
Labourer
Posts: 2
Joined: Wed Apr 25, 2007 8:24 am

by newartist » Thu Apr 26, 2007 1:10 pm

Thanks for that most helpful, you say about plastic pipework, what about plastic speedfits connecting the different pieces of copper pipework, would you have to earth bond each individua copper l pipe looping the earths together?

Alan

3 posts   •   Page 1 of 1
It is currently Mon Nov 04, 2024 8:55 pm