by Jeffmo »
Wed Apr 25, 2007 2:51 pm
the original shower blew its fuse , are you saying you have two showers in the house. When you had the new shower fitted ,was it a plumber or an electrician that fitted it all ie plumbing and wiring .? If things start blowing fuses then its not really enough just replacing the fuse , there must be a cause and its this that you need to find . Regards the new one , there should be a label in the consumer unit that simply says 'shower ' if there isn't then the cable should be at least 6mm cross sectional diameter , if there are no thick cables in the cu then you have serious problems and definately need an electrician , if the shower is rated at anything over 8kw then the cable needs ideally to be 10mm , over 9 kw ideally 16mm cable and on dedicated circuit ( separate mcb/fuse ) Like i said best get someone in before the undertaker has to call . Best regards and good luck Jeff