Out of interest the regulation is:- 513 ACCESSIBILITY
513.1 Except for a joint in cables where Section 526 allows such a joint to be inaccessible. every item of equipment shall he arranged so as to facilitate its operation, inspection and maintenance and access to each connection. Such facility shall not he significantly impaired by mounting equipment in an enclosure or a compartment.
526.3 Every connection shall be accessible for inspection, testing and maintenance, except for the following:
(i) A joint designed to he buried in the ground
(ii) A compound-filled or encapsulated joint
(iii) A connection between a cold tail and the heating element as in ceiling heating, floor heating or a trace heating system
(iv) A joint made by welding, soldering, brazing or appropriate compression tool
(v) A joint forming part of the equipment complying with the appropriate product standard.
The main point is the joint could comply with list in 526.3 and to rip apart a house in case it does not apply is unreasonable. we are suppose to do non destructive testing and where for example dimming switches are fitted we don't do insulation test at 500 volt. We also have to indicate severity of faults BPG4_08.pdf is a document giving the codes and there are 4 of them.
Code 1 Requires urgent attention.
Code 2 Requires improvement
Code 3 Requires further investigation
Code 4 Does not comply with the current issue of BS 7671
He could use Code 3 but the document points out the purpose of periodic inspection is not to carry out a fault-finding exercise, but to assess and report on the condition of the installation within the agreed extent and limitations of the inspection. That is a quote from the Electrical Safety Council document. Try an internet search for BPG4_08.pdf I am sure you will find link.
All best Eric