by ericmark »
Sat Mar 29, 2008 7:19 am
Much depends on what is in the bathroom. And what version of the regulations the house has been wired to the old 16th Edition said:-
601-04 Supplementary equipotential bonding
601-04-01 Local supplementary equipotential bonding complying with Regulation 547-03 shall be provided
connecting together the terminal of the protective conductor of each circuit supplying Class I and Class II equipment
in zones 1, 2 or 3, and extraneous-conductive-parts in these zones including the following:
(i) metallic pipes supplying services and metallic waste pipes (e.g. water, gas)
(ii) metallic central heating pipes and air conditioning systems
(iii) accessible metallic structural parts of the building; (metallic door architraves, window frames and similar
parts are not considered to be extraneous-conductive-parts unless they are connected to metallic structural
parts of the building)
(iv) metallic baths and metallic shower basins.
The supplementary equipotential bonding may be provided in close proximity to the location.
But the new 17th Edition says:-
Where the location containing a bath or shower is in a building with a protective equipotential bonding system in accordance with Regulation 411.3.1.2, supplementary equipotential bonding may be omitted where all of the following conditions are met:
Because it depends on if earth leakage devices are installed and what electrical items are in your bath room plus the amount of plastic pipe. It is not possible to give a single answer but I would suspect that you will not need that earth wire. The idea is to make it so while wet you can't touch items having different voltages and to ensure this all items which could carry current are connected together. But they are not connected directly to incoming earth although they may be indirectly connected. So to tell you to connect the earth wire you have to anything could be wrong as we don't know what the other end is connected to. I will point out there is a link to Part P on projects page and this does also give some information. I am loathed to try to tell you what to do in case you have missed something which could change what is required. One does really need to be on site to give advise of this nature.