by zygo »
Tue Apr 08, 2008 8:57 am
First and foremost, ericmark, good luck in the exam! And secondly, thanks for the July 08 warning. If I read this correctly, however, I won't be affected by it. As the existing main CU is in the garage, and the small one I want to install is also in the garage, the cable linking them will be surface mounted so I think this means it will not need to be protected by an RCD. Of course, I could connect it to one of the MCBs on the (RCD) protected side of the main CU. This would mean that anything on the MCBs in the new CU would be doubly RCD protected (first by the RCD in the new CU and then by the RCD protecting the MCB in the main CU). Would that be desirable or cause a problem.
One final thing, would the small CU need to have its own direct earth connection - I was thinking that a 40A T+E cable link would allow me to use the earth of the main CU (which, of course, is itself earthed by a link to a water pipe).
Keep on studying! (unless you took the exam a while ago and are simply awaiting the result, in which case good luck with the result!)