For the amount of water you're losing leak sealer wont work.
It could be a few things, a leak under the floor downstairs (if there's any pipes there. As if it was upstairs you would have noticed by now.
Does the water discharge via the pressure relief valve ? maybe the PRV is passing
Does the pressure rise ? could be the expansion vessel or the plaste heat-exchanger - again the pressure would rise and discharge via PRV.
Any decent engineer would have checked all of the above.
So my bet is - and i've had a few boiler where this has happened (if it is a condensing boiler) the secondary heat-ex is split the water will be lost via the condensate discharge pipework.
Check the condensate pipework for excessive water discharge - quite difficult to diagnose as there will be water discharging if the boiler is on. Try with the boiler off - any running water ?
Hope this helps