Hi Tara,
as usual Eric has covered almost everything, only thing I will add is costing for PIR.
We do lots of them for landlords & owners & have worked out a formula for quotes 'unseen'!
We charge basic £70 to inspect mains, earthing, bonding, test sheets, plus £22/circuit.
Giving a scale of rates for the customer to work out ie 4 circuits = £148.00
6 = £192.00, 8 = £236.00
on each circuit we inspect a % of lights, switches, skts as appropriate.
carry out insulation, earth continuity, polarity, earth fault loop, and if fitted RCD tests.
We give on the report as Eric says, catagories of non conformities as standard ie
[1] requires urgent attention.....(unsafe/dangerous-will leave switched off)
[2] requires improvement.........(not to regs, may lead to overload say)
[3] requires further investigation.(unable to locate circuit or broken ring)
[4] Does not comply with currect standard regs, (every house not wired to 17th edition after 10/17/2008!!!!!(does not imply installation unsafe)!
Whether or not you need a consumer unit change will depend upon recommendation in PIR which is main reason for investing in one, unfortunately it is one of the bit of the dreaded HIP's that was dropped or it would have been done as a matter of course by the vendor.....got it wrong again GORDON!!!
regards SPARX