by Edwardlanson »
Mon Apr 28, 2008 2:32 pm
I have a fully pumped CH/HW system with a room thermostat, a cylinder thermostat (HTS3) and a mid-position actuator (Drayton MA1). Recently I noticed that the boiler kept cutting out even though the pump was still on and, after further investigation, it appears that the hot water is never satisfied and that the boiler was just cutting out as it was getting too hot. The CH on its own is working OK, the actuator appears from the outside to be working OK, i.e. the levers are moving to W, M, H as appropriate. I tried to turn the cylinder stat 'off' but the dial wouldn't turn so I assumed the stat was faulty and replaced it. This has made no difference. On the new stat, the dial can be turned to off and this will switch off the boiler and pump. However, even with it set at its lowest temp (50C), and after the HW has been on for 50 mins and is piping hot, turning the programmer on to HW always calls for it and it is never satisfied. I am trying to eliminate the actuator as a problem so does anyone know if the 'off' position on the stat dial is the same as 'satisfied' or does it work differently? The actuator is only 15 months old. Any ideas on what might be wrong? This set-up has worked perfectly well until now so it is unlikely to be wrongly wired, for example.