Hot water only works when Heating is on - Ideal minimiser

by rthom1 » Thu May 22, 2008 4:03 pm

I have a systen boiler Ideal minimiser SE. I can only get hot water when the Heating is on! (it didnt used to be the case) If i put the hot water on alone, it doesnt fire up the boiler. If the C/H is on then i get hot water when i turn the water on. I tried changing the programmer but that had no effect. I can hear the diverter valve moving when i turn thr water on and off . Any ideas anybody????

rosebery
Project Manager
Project Manager
Posts: 2021
Joined: Wed Sep 26, 2007 9:55 pm

by rosebery » Sat May 24, 2008 12:14 am

If the 3 port valve is operating your description suggests you have a duff cylinder stat.

Hang on a mo though. What temp is the stat set to? Try turining it up and seeing if anything happens.

Cheers