by ericmark »
Mon Jun 02, 2008 11:31 pm
Min size of any earth cable no protected is 4mm² 543.1.1 (v) + 544.2.1
The PEN cable has a min size of 10 mm² 543.4.3 (Not really anything to do with you)
Main protective bonding conductor min 6 mm² 544.1.1
Where PME conditions apply it is dependent on supply cable min 10 mm² Table 54.8
Remember I have quoted min sizes from BS 7671:2008 the old BS 7671:2001 may differ. There are other regulations like 543.7.1.3 high conductor currents min 10 mm² since you do not give all details you will have to verify which is why I give regulation number. As kbrownie has said it may not be required I can’t find anything in BS 7671:2008 about sinks and toilets only baths, showers, saunas, swimming pools, and fountains. But you must follow manufactures instructions so if for example the grinder says you need an extra earth then you do need it.
All best Eric