Glow Worm 18Si

by shearo » Tue May 20, 2008 6:54 pm

Could anyone shed any light as to why my boiler has started to lose pressure? I have to re-pressurise almost everyday.I've bled the rads several times.......
Thanks

plumbbob
Project Manager
Project Manager
Posts: 1892
Joined: Wed May 07, 2008 10:59 pm

by plumbbob » Tue May 20, 2008 9:01 pm

You have a leak somewhere on the heating system. You will have to examine all the pipework to find the escape.

shearo
Apprentice
Apprentice
Posts: 7
Joined: Tue May 20, 2008 6:51 pm

Glow-worm 18Si

by shearo » Thu May 22, 2008 7:52 am

Thanks for that Plumbob...I've had a look and as yet cannot find a leak could it be something inside the boiler itself like a saftey valve blowing off???????

plumbbob
Project Manager
Project Manager
Posts: 1892
Joined: Wed May 07, 2008 10:59 pm

by plumbbob » Thu May 22, 2008 5:24 pm

There is a small copper pipe that will go through the wall to outside somewhere near the boiler see if that is dripping. It is not impossible for the boiler to be leaking internally, but there are more likely places for leaks to occur.

Remember you have a sealed system, and only a very small leak will cause the pressure to drop. Probably a mug full is sufficient so if the leak is slow, most of the water will evaporate and leave little trace.

Check radiator valves and the carpet or flooring where water might drip. Then examine closely any exposed pipework and joints.

You cold try a leak sealer, but I would exhaust every other route first.

shearo
Apprentice
Apprentice
Posts: 7
Joined: Tue May 20, 2008 6:51 pm

by shearo » Tue Jun 03, 2008 7:50 am

Hey Plumbob...my boiler is leaking outside! I finally witnessed this , this morning. So what has gome wrong any ideas??? Many Thanks

htg engineer
Project Manager
Project Manager
Posts: 3256
Joined: Tue May 22, 2007 6:22 pm

by htg engineer » Tue Jun 03, 2008 4:51 pm

Heating on ? pressure rising - expansion vessel needs re-pressurising or replacing.

Heating off ? pressure rising - hole in plate heat-exchanger - or mains and heating water mixing.

htg

adamjoner
Labourer
Labourer
Posts: 2
Joined: Tue Jun 03, 2008 9:45 pm

by adamjoner » Tue Jun 03, 2008 10:10 pm

hi shearo,
if u have noticed the boiler leaking to outside, then the pressure relief valve is passing and needs replacing, it could also be the charge of the pressure vessel which will allow the pressure to rise above recommended pressure 3bar when the boiler is in use, hope this helps

shearo
Apprentice
Apprentice
Posts: 7
Joined: Tue May 20, 2008 6:51 pm

by shearo » Wed Jun 04, 2008 3:38 pm

Thanks adam I've just re-pressurised the system to 2 bar and without anything turning on I noticed the water coming out of the outside pipe.also the pressure has gone down...not surprisingly I suppose?????

TheDoctor5
Posts: 1381
Joined: Tue Jan 20, 2009 9:17 am

by TheDoctor5 » Tue Jan 20, 2009 10:10 am

Last year 64% of the questions asked in our forum were answered within our DIY project pages at www.diydoctor.org.uk/projects.htm The project pages are now separated alphabetically and your answers are accompanied by diagrams and the ability to see, and buy, the tools and/or required to complete your project. Use our search box to look for your answer and save a great deal of time and money!