by ericmark »
Thu Jun 26, 2008 11:17 pm
It comes from Part M if you follow links in projects to Part P you can find the other Parts including M.
It says:-
Page 48
Switches, outlets and controls
Design considerations
4.25 The key factors that affect the use of switches, outlets and controls are ease of operation, visibility, height and freedom from obstruction. However, there will be exceptions to height requirements for some outlets, e.g. those set into the floor in open plan offices.
Provisions
4.30 Switches, outlets and controls will satisfy Requirement M1 if:
a. wall-mounted sockets outlets, telephone points and TV sockets are located between 400mm and 1000mm above the floor, with a preference for the lower end of the range;
b. switches for permanently wired appliances are located between 400mm and 1200mm above the floor, unless needed at a higher level for particular appliances;
c. all switches and controls that require precise hand movements are located between 750mm and 1200mm above the floor;
d. simple push button controls that require limited dexterity are not more than 1200mm above the floor
e. pull cords for emergency alarm systems are coloured red, located as close to a wall as possible and have two red 50mm diameter bangles, one set at 100mm and the other set between 800 and 1000mm above the floor;
f. controls that need close vision are located between 1200mm and 1400mm above the floor so that reading may be taken by a person sitting or standing (with thermostats at the top of the range);
g. sockets outlets are located consistently in relation to doorways and room corners, but in any case no nearer than 350mm from room corners;
h. light switches for use by the general public have large push pads and align horizontally with door handles within the range 900 to 1100mm, for ease of location when entering a room;
i. where switches described in 4.30(h) cannot be provided, lighting pull cords are set between 900mm and 110mm above floor level, and fitted with a 50mm diameter bangle visually contrasting with its background and distinguishable visually from any emergency assistance pull cord;
j. switched socket outlets indicate whether they are ‘on’;
k. mains and circuit isolators switches clearly indicate that they are on or off;
l. front plates contrast visually with their backgrounds.
I do not see this talking about consumer units and not sure they have to have wheel chair access see what you think?