Why do we use B and C type MCB's?
A D type MCB trips at 20 times the rated value.
So 230/(Rated value x 20) = Max resistance of cable.
Also 230 x 5%/Rated value = Max resistance of cable.
Since divide by 20 = 5% the limit due to current required to trip a D type MCB is same as the limit due to volt drop of 5% before the 17th Edition B and C type MCB's would be used because of the earth loop impedance but with RCD's taking care of that I would have expected B and C type MCB's would have very little place and would just cause nuisance tripping? Especially in lighting circuits with 3% volt drop and often tripping the MCB when the light emitting devices blow.
I can see to protect equipment we may need B and C types but not to protect the installation.
So what have I missed?
My error has been pointed out using D type could blow the incoming fuse so other than for very low rated MCB's such as for lights we should not use C or D rated. I still invite any comments I want to design a spreed sheet to make the Schedule of test results and at the same time test for anything which is wrong with the results which is why I posed the question.
Eric