by sparx »
Sat Jul 26, 2008 9:59 pm
Hi all.
a couple of other points to bear in mind,
1] part L of building regs insists that where control is by TRV's one area must have rad without one and a room stat must be fitted in that area to prevent boiler cycling on & off, this can be combined with timer ie programmable room stat.
2]not only SIME boilers that need relay. All BOSCH Worcester combi & system boilers need the controls external to boiler to be fed from boiler ie
not correct to take perm. live and switched live & Neutral & earth from external controls direct to boiler. It will work but it bypasses all the boilers internal safety circuits!!!
Correct way is to fit relay contacts in place of internal link Ls-Lr, then use sw.line to relay coil and coils N to spare N term on connector plug.
This confirmed by B-W tech. help line, if you connect these boilers you will know the set up,
regards SPARX